Subject: The Worst Tank Installation Ever?
You are not authorized to post a reply.
Author Messages
stevem
Posts:152

Consultant
01/03/2009 11:17 AM Alert 

Thanks to Tom Dunbar of Charlotte Monitoring Systems.  Go to the Photo Gallery at http://new.petrolsmart.com/Gallery/tabid/56/Default.aspx and click on "Bad Elutron Plasteel Tank Installation" to see the pictures after you read below. 

Sent: Tuesday, December 16, 2008 9:05 AM

Subject: Installation criteria for the Plasteel Elutron Underground Tank

Mr. Sharpe,

 As explained yesterday, I was wondering if the Petroleum Contractor is following the proper procedure for the tank installation. During the installation inspection, I noted several issues at the facility. Please see the above referenced photos.

 The issues are as follows:

 1. The contractor was pushing the tank down with a large track hoe filled with concrete and dirt. The contractor explained that due to the high water table and because the excavation site was not shored, mud was caving in the hole and raising the tank (see photos).

 2. A large scratch was present on the east side of the tank. The blue color of the FRP laminate was showing a white fractured pattern (see photo).

 3. Also, several scratches were observed on the north side of the tank where the track hoe was actively pushing the tank down. The blue color of the FRP laminate was showing a white fractured pattern (see photo).

 4. When I initially asked the contractor if a vacuum was present on the interstice when the tank was delivered, he could not answer me. The tank gauge on the interstice was reading zero. The contractor could not inform me if he released the vacuum & whether the vacuum was release before or after the tank was installed (see photos).

 5. I explained to the contractor that the bedding material was much too large. He assured me that it was an acceptable material according to the installation criteria. The bedding material installed under the tank was an inch to inch and a half landscaping aggregate. Some of the aggregate was as large as 2 inches. A sample of the material was collected by the Department (see photos).

 Any information you could provide the Department on this matter would be greatly appreciated. Thank you.

 David Lee Pears

Environmental Specialist II

Charlotte County Storage Tank Program

Charlotte County Health Department

Tom Dunbar
Posts:8
Contributor
01/11/2009 6:59 AM Alert 
Just an update on this job. We had a 3rd party test this tank and it failed a vac test. It also was found to have approx 36 inches of water in the interstitial space (SURPRISE)!

The contractor then tried to convince the owner of the tank company that he has no idea how the tank was damaged and it must have been damaged in transit. The owner had already seen this email with the pictures!!!
This tank was sent back and a new one was ordered.

Lee County has had issues with this contractor also.

Beware of Moonlight Construction
Tom Dunbar
Posts:8
Contributor
01/26/2009 4:32 PM Alert 
Update #2
The contractor tried to set the new tank and finally stopped before the store fell into the hole. He filled in the hole and has hired another contractor to install shoring.
Tom Dunbar
Posts:8
Contributor
01/29/2009 4:04 PM Alert 

Update #3 & 4

Well he finally got this tank installed on Wednesday the 28th.  It had a tilt of about 4 inches and is off center 4-6".  I don't think you can install the fills properly or even stick it.

 

BUT NOT TO WORRY!!

Today they stated to pull the shoring out and after the 4th panel was removed the tank popped out of the ground.  He did not fill the tank with water!!   Pulled the eye bolt out of the deadman and broke the tie down straps.

Tonight as I drove by the tank is setting in the parking lot.

More to come.

Tom